Applies to:
Gas Heat System Sequence of Operation
This product is in test and not for sale at this time.
Heat Demand Initiated
-
Triggered by user command to Preheat or Start Cook Cycle.
-
GMU (Gas Management Unit) begins heat sequence.
Safety Circuit Check
-
GMU verifies the following are closed:
-
Electronic Fuse (U9) – Must be closed to proceed.
-
High Limit Circuit – Must be below trip point (430°F).
-
Combustion Fan Pressure Switch – Must be open before fan starts.
-
Tech Tip: If the fan doesn’t engage after step 3, check the high-limit switch.
Combustion Fan Activation
-
GMU sends 24V DC signal to Blower Control Board (BCB).
-
BCB closes and sends line voltage to combustion fan.
Expected Behavior: You should hear the fan motor engage.
Pressure Switch Verification
-
Fan airflow closes the normally open pressure switch.
-
GMU confirms switch closure to proceed.
Troubleshooting Cue:
-
E-20A: Pressure switch failed closed.
-
E-20B: Pressure switch failed open.
Gas Supply Enabled
-
Non-CE Units: Gas flows directly to combination valve.
-
CE Units: GMU sends 24V AC to Safety Shutoff Valve, allowing gas to reach pilot valve.
Pilot Ignition
-
GMU sends 24V AC to Ignition Module (TH terminal).
-
Ignition Module:
-
Sends PV signal to GMU.
-
Sends high-voltage spark to pilot electrode.
-
-
GMU sends PV signal to pilot solenoid, opening gas flow to pilot.
-
Pilot flame ignites and is verified by flame sense rod.
Expected Behavior: You may hear a clicking spark followed by a soft flame ignition.
Main Burner Ignition
-
With pilot flame confirmed, Ignition Module sends MV signal to GMU.
-
GMU sends MV signal to main solenoid, opening gas flow to burners.
-
Burners ignite and heat exchanger tubes transfer heat to oil.
Expected Behavior: You should hear a steady burner flame.
Flame Rollout Monitoring
-
J-type thermocouple above burner entrance monitors flame behavior.
-
If flame rollout is detected:
-
GMU triggers E-20R error.
-
Gas heat system shuts down until error is acknowledged.
-
Key Spec and Notes
-
Full Vat Output: 75,000 BTU/hr (gross), 19.8 kW (net)
-
Split Vat Output: 37,500 BTU/hr (gross), 9.9 kW (net)
-
High Limit Trip Point: 430°F (221°C)
-
High Limit Reset Point: 374°F (190°C)
-
Pressure Switch: Normally open, closes with fan airflow
-
Flame Sense: Requires ≥1 micro-amp DC current to confirm pilot flame
Related Content
Control MAP Theory of Operation
Control MAP Sequence of Operation
GMU Hi Limit PCB Theory of Operation
Gas Heat System Theory of Operation
Filtering Sequence of Operation
Cart Dispose System Theory of Operation
Cart Dispose System Sequence of Operation
Bulk Oil System Theory of Operation
Bulk Oil System Sequence of Operation
ATO System Theory of Operation
ATO System Sequence of Operation
Reference