Troubleshooting the E-20 (J-K) PV2/MV2 Jumper Missing (Split Vat Only) Error Code
Overview
E-20 J - PV2 Jumper Missing (Split Vat Only)
This error occurs when the ignition module wiring harness is missing the PV2 configuration jumper. On split-vat units, the PV2 jumper is required to inform the GMU (Gas Management Unit) that a second pilot valve circuit is installed.
If the jumper is missing, disconnected, or the incorrect wiring harness is installed, the controller will generate an E-20 J error.
E-20 K - MV2 Jumper Missing (Split Vat Only)
This error occurs when the ignition module wiring harness is missing the MV2 configuration jumper. On split-vat units, the MV2 jumper is required to inform the GMU that a second main valve circuit is installed.
If the jumper is missing, disconnected, or the incorrect wiring harness is installed, the controller will generate an E-20 K error.
Call Avoidance Steps
Before dispatching a service technician, perform the following checks:
-
Verify the fryer is configured as a split-vat unit.
-
Verify in Information>About This Fryer.
-
-
Turn the unit OFF and then back ON to confirm the error is still present.
-
If error persists, a service call will be required.
Field Troubleshooting
-
Correct split-vat ignition module wiring harness (if incorrect harness is installed)
-
Digital multimeter
-
Basic hand tools (screwdrivers, nut drivers, etc.)
Troubleshooting Steps
-
Verify the displayed error is E-20 J or E-20 K.
-
Determine whether the fryer is a split-vat configuration.
-
If the fryer is not a split-vat unit, verify the proper configuration and harness are installed.
-
If the fryer is a split-vat unit, continue to Step 3.
-
-
Turn OFF power to the fryer.
-
Access the ignition module and wiring harness.
-
Inspect the ignition module harness for the PV2 configuration jumper or MV2 configuration jumper.
-
If the jumper is present and properly seated, continue to Step 6.
-
If the jumper is missing, reinstall or replace the jumper, then go to Step 8.
-
-
Verify the installed wiring harness matches the required harness for a split-vat fryer.
-
If the correct harness is installed, continue to Step 7.
-
If the wrong harness is installed, replace it with the correct split-vat harness and then go to Step 8.
-
-
Inspect the jumper and harness connections for damage, loose terminals, or poor contact.
-
If damage is found, repair or replace the affected component and then go to Step 8.
-
If no damage is found, continue troubleshooting according to standard ignition module diagnostic procedures.
-
-
Restore power to the fryer.
-
Clear the error and restart the unit.
-
Verify operation.
-
If the error is cleared, return the fryer to service.
-
If the error remains, replace the ignition module harness with a known-good split-vat harness and retest.
-
If the error still remains after harness replacement, replace GMU Board.
-
Other Troubleshooting
-
A standard (non-split-vat) harness may have been installed during a previous repair.
-
The jumper may be present but not fully inserted into the harness connector.
-
Harness terminals may be damaged, bent, or backed out of the connector.
-
Intermittent vibration-related connection issues may cause the jumper to lose contact.
-
In rare cases, the GMU may incorrectly detect the jumper status due to an internal fault. Verify all wiring and harnesses before replacing control components.
Related Content
Troubleshooting an E-4 Error VIU/OMS/GMU Board Overheating
Troubleshooting an E-5 Oil Too Hot Error Code
Troubleshooting an E-6 (A-B) Temperature Probe Failed Error Code
Troubleshooting an E-10 High Limit Error Code
Troubleshooting the E-20 (A-B) Pressure Switch Stuck Closed/Open Error Code
Troubleshooting the E-20 C Pilot Valve Signal Not Detected Error Code
Troubleshooting the E-20 D Gas Ignition Failure No MV Signal Error Code
Troubleshooting the E-20 M GMU Relay Failure (MV) Error Code
Troubleshooting the E-20 S Safety Relay Failure Error Code
Troubleshooting an E-22 No Heat Error Code
Troubleshooting the E-21 Slow Heat Recovery Error Code
Troubleshooting the E-93T Transformer 24 VAC Failure/Not Connected Error Code
Replacing Temperature and Level Probe
Replacing Blower Control Board
Reference